OK,
in relation to an ongoing thread in another part of the forum I thought I'd put a question in here,
this is an actual real world situation, my own house, so, as you may have guessed I have already made the answer up,
but, I would like you guys to tell me why, and how, and what you would do.
as an aside, the earthing arrangement is perfectly fine to export the TNCS on, if you need any more info regarding that particular aspect then I can provide that, but it is not relevant to the cable sizing , OCPD etc .
what size OCPD do I need to supply my shed?
what protection do i need to provide?
there will be a mini pvc CU fitted to the shed.
TNCS incomer
100A main switch
6mm T&E >50mm from the surface of any wall [ 12m length ]
surface clipped not in contact with any insulation
changes to 10mm 4core SWA for outside run @ 12m length , 2 cores are redundancy so CANNOT be used for anything else, but loading on them CAN be ignored for the purposes of this exercise.
the cable is already installed so is non change-able, you have to work out the max permissable loading and what protection I require.
any help?I cant find a limiting factor other than It, although this leaves next to nothing VD wise for the final circuits.
Obviously cant do shock and thermal constraints.
is it that simple considering the resistance of the cable and the likely type of loading? not simply the max load.