Hi all, hope you are well.
I did a PIR in a domestic dwelling today.
With power off I recorded Ze (TNS) as 0.08 ohms (transformer quite close).
The voltage measured on the incoming tails was 232V AC.
Yet when I measured PFC I kept getting 19.9KA.
Puzzled with the very high reading, I thought I would calculate it to check the reading so I divided the Ze by the voltage, ie 232/0.08.
The result was 2.9KA.
Have I done something wrong or do you think my multitester is playing up?.
If the PFC is indeed 19.9KA then what should I do with the MCB's as they are rated at 6KA. The main fuse is a BS1361 60A..... so PFC of that is about 16KA I think..........
Any thoughts greatly appreciated
Best Regards
RUS
I did a PIR in a domestic dwelling today.
With power off I recorded Ze (TNS) as 0.08 ohms (transformer quite close).
The voltage measured on the incoming tails was 232V AC.
Yet when I measured PFC I kept getting 19.9KA.
Puzzled with the very high reading, I thought I would calculate it to check the reading so I divided the Ze by the voltage, ie 232/0.08.
The result was 2.9KA.
Have I done something wrong or do you think my multitester is playing up?.
If the PFC is indeed 19.9KA then what should I do with the MCB's as they are rated at 6KA. The main fuse is a BS1361 60A..... so PFC of that is about 16KA I think..........
Any thoughts greatly appreciated
Best Regards
RUS