Can anyone shed some ligh on why I got the following readings? This all started with a phonecall from a plumber who had got an electric shock from a washing machine he had to pull out. The house owner got a appliance repair man to check the washer which he said was ok. I checked the incoming supply and found that it was a TNS system with a wylex fuse board containing 3036 fuses. The gas and water were bonded, the continuity of the bonding was ok. The house had new gas central heating fitted. I checked the voltage between the copper piping of the heating system and it was 0. I then checked between the earth terminal of a nearby socket and the copper pipe of the heating system and got 63v. This occured on every socket to the pipework. I then checked the sockets and got the following readings
P-E 136V, P-N 247v, N-E 136V.
I checked the R1,R2 Rn and they were ok. Insulation tests were also ok. Only the sockets were affected. I then 'reassembled' the circuit and retested everything only to find everything now tested ok. Started to plug household appliances in and still got good readings the fault seems to have gone. Any ideas what could have caused these readings, only thing I could find was the cpc in the consumer unit was not tightened. I'm stumped
P-E 136V, P-N 247v, N-E 136V.
I checked the R1,R2 Rn and they were ok. Insulation tests were also ok. Only the sockets were affected. I then 'reassembled' the circuit and retested everything only to find everything now tested ok. Started to plug household appliances in and still got good readings the fault seems to have gone. Any ideas what could have caused these readings, only thing I could find was the cpc in the consumer unit was not tightened. I'm stumped