Do you have to measure R1 + R2 readings or is it acceptable to take live ZS reading and deduct the ZE reading ?
I thought that was the case. I always do but a new spark that started working with my boss said to save time deduct the Ze. I said you shouldn’t but he said I was just a Squeaky clean newbie, so wanted your thoughts. Thanks all makes sense. Cheers chapsOne theoretical example: Old house, central heating pump has a FCU, You test Zs at that point, reading within spec for the protective device. Deduct Ze from Zs, fill out your R1+R2 on the cert. A week later along comes the plumber and puts a load of plastic pipe in. you're unlikely to go back again for another 5 years but say you did go back after the plumber, do your Zs again open circuit because the cpc has been open circuit all along but you were getting a reading through the earthed metallic pipework which the plumber has kindly now removed..
You haven't proved continuity of conductors doing it the way you mention. You could be getting a Zs reading from a parallel path that could later be removed. Most of all it's just lazy, do your R1+R2 or R2 properly.
Easier said than done I would think.Leave said company and find a proper one.
Yes Geoff your right . Got a placement so I’m sticking with it but questioning everything I’m learning so much by doing so.Easier said than done I would think.
If you get an opportunity then grab it, but otherwise I would say maintain your questioning approach and keep your standards high whatever others do.
The only stupid question is the one you don't ask!t questioning everything :-)
respect for perseverance, one day you’ll be able to look back with pride that you learned to ignore all the bad habits you’ve been shown.Yes Geoff your right . Got a placement so I’m sticking with it but questioning everything I’m learning so much by doing so.
Do you have to issue a minor works certificate ?
I know about notifications and when to and also EIC’s. But if say change a light fitting or add a socket do you have to issue a Minor works ? My colleague seem to think you don’t have to issue them. Is this lazy or the done thing ?
Unless you use a Megger and there's the option for the MFT to do it for you...you can calculate Zs from Ze + R1R2 but you cannot calculate R1R2 from Zs-Ze
Unless you use a Megger and there's the option for the MFT to do it for you...
Thanks chaps. Another thing I just wanted clarity on please.
Do you have to issue a minor works certificate ? I know about notifications and when to and also EIC’s. But if say change a light fitting or add a socket do you have to issue a Minor works ? My colleague seem to think you don’t have to issue them. Is this lazy or the done thing ?
An excellent question I would like to answer...How does the Megger rule out parallel paths?
Just curious
An excellent question I would like to answer...