I have seen similar faults on the past.
One turned out to be a capping nail through that nicked a live core of a T&e. Caused nuisance tripping when it rained.
And I have seen a neutral on an rcd ring circuit cross connected to the neutral on a non rcd lighting circuit. That also caused nuisance trips.
I would suggest doing an ir test on the installation as a whole and seeing what value you have. If all the appliance are testing out ok, then the earth leakage causing the rcd to trip must be coming from the wiring.
If that all test out fine then I'd be testing for continuity between the neutrals of all the circuits...see if you have a random cross connect somewhere.