Hello, I am hopeful that somebody can give me some info with regard to RCBs and MCB since I have a small problem (I think), details as follows:
I have a MK consummer unit populated with RCBs and MCB and I am extending the lighting circuit which is protected by a 6amp MCB.
Before extending the cable I switched off the 6A MCB and commenced work, during the work, the earth and neutral wires touched and the RCB tripped, which surprised me somewhat. I reset the RCB and checked the voltage between the earth and neutral and there is nothing to speak about but each time I short out the earth and Neutral the RCB trips. Is this normal? I had assummed that earth and neutral would be at the same potential. Any help would be greatly appricated.
Ian
Perfectly normal I doubt there isn't an electrician about who hasn't had it happen to them.
Yep, all normal. Technically created an earth fault between earth and neutral. An MCB only isolates the Line (Live) conductor.