Once again, some wonderful words of wisdom (not) ........... allowed to go unchecked.
As the loads increase, so does the earth-leakage........eventually tripping the RCD.
So when PC says this.......
If it was a wiring fault then the RCD would be tripping irrespective of what is plugged in.
Neutral / Earth faults are load specific - so won't trip an RCD with all loads disconnected.I would think if there were a wiring fault, it would trip even with NOTHING plugged in.
As the loads increase, so does the earth-leakage........eventually tripping the RCD.
So when PC says this.......
........he is probably 100% correct.My money's on a highish resistance N-E fault. Possibly in the wiring or an appliance that's permanemtly plugged in (fridge, washer etc).In these cases an IR of the circuit should be at the top of the test list.