Ok heres a bit of bumff wot the NICEIC say:-
A means for automatic disconnection of supply, such as a fuse or a contact of an overcurrent circuit-breaker or RCD, is to be inserted in the line conductor of a single-phase circuit and in every line conductor of a multi-phase circuit. The fuse or contact must be arranged to open in the event of an earth fault affecting the line conductor concerned, in accordance with the requirements of BS 7671 for automatic disconnection (see item 6).
There is no general requirement in BS 7671 for means to be provided for automatic disconnection of a neutral conductor. However, there are a number of exceptions. Examples of where a circuit-breaker or RCD must be of the multipole type which disconnects all line conductors and the neutral conductor are as follows:
The overcurrent protective device of each final circuit in a caravan or motor caravan (Regulation 721.43.1 refers).
Where selected as a main switch for operation by ordinary persons for a single-phase supply, such as in a household or similar installation (Regulation 537.1.4 refers).
Where selected as a means of isolation for a circuit in an installation forming part of a TT system (Regulation 537.2.1.1 refers).
Where selected as a means of isolation for a circuit in an installation in a potentially explosive atmosphere (in order to avoid the possibility of incendive sparking), clause 8.2 of BS EN 60079-14 refers.
Any circuit-breaker or RCD which is inserted in an earthed neutral conductor must be of the linked type, arranged to break all the related line conductors (Regulation 132.14.2 refers).
A single-pole fuse, circuit-breaker or RCD is not to be inserted in a neutral conductor, but only in the line conductor (Regulation 132.14.1 refers).
It is generally sufficient for overcurrent protective devices and RCDs to be of the single-pole type (inserted in line conductors). However, there are exceptions,
Examples of where a circuit-breaker or RCD must be of the multipole type disconnecting all line conductors are as follows:
An RCD used in a circuit having more than one line conductor (Regulation 531.2.1 refers).
In a circuit supplying a multi-phase motor (for example, three-phase), if necessary in order to avoid