Hi everybody. First time post so please be gentle...
I have just been to a house after a friend of mine has appeared to uncover a fault with a Crabtree 3 module RCD on a split load board that keeps tripping out when he plugs in a small air con unit that he has just installed. But with the air con unit unplugged it seems to have awoken an issue with the RCD
I have been and done an IR test (with air con still unplugged) on all circuits and the lowest reading between N & E is about 43MΩ so shouldn't give me a problem with nuisance tripping. The RCD behaves quite erratically when all circuits are on, i.e. it sometimes works well on a ramp test and sometimes trips out on half rated. So you'd think that I just change the RCD and everything would be ok. I ordered one of Ebay and fitted it....and got the same problem. Now I know that sometimes you can get dodgy stuff from Ebay, and you take your chances and all that, and I have now ordered a brand new one from my wholesalers but have 2 questions -
1. The IR reading between the neutral bar of the non RCD side and the neutral bar of the RCD side is about 80MΩ. Surely this wouldn't make a difference?
2. Are these older Crabtree ones really that good? Whenever I have any RCD issues it always seems to be flippin' Crabtree.
Also, I could get the RCD to trip out just by passing a screwdriver tip by the front of the housing but without actually touching it. Obviously the coil wasn't liking metal close by.
Any help or opinions would be greatly appreciated. Thanks
I have just been to a house after a friend of mine has appeared to uncover a fault with a Crabtree 3 module RCD on a split load board that keeps tripping out when he plugs in a small air con unit that he has just installed. But with the air con unit unplugged it seems to have awoken an issue with the RCD
I have been and done an IR test (with air con still unplugged) on all circuits and the lowest reading between N & E is about 43MΩ so shouldn't give me a problem with nuisance tripping. The RCD behaves quite erratically when all circuits are on, i.e. it sometimes works well on a ramp test and sometimes trips out on half rated. So you'd think that I just change the RCD and everything would be ok. I ordered one of Ebay and fitted it....and got the same problem. Now I know that sometimes you can get dodgy stuff from Ebay, and you take your chances and all that, and I have now ordered a brand new one from my wholesalers but have 2 questions -
1. The IR reading between the neutral bar of the non RCD side and the neutral bar of the RCD side is about 80MΩ. Surely this wouldn't make a difference?
2. Are these older Crabtree ones really that good? Whenever I have any RCD issues it always seems to be flippin' Crabtree.
Also, I could get the RCD to trip out just by passing a screwdriver tip by the front of the housing but without actually touching it. Obviously the coil wasn't liking metal close by.
Any help or opinions would be greatly appreciated. Thanks