I have just been to a house after a friend of mine has appeared to uncover a fault with a Crabtree 3 module RCD on a split load board that keeps tripping out
The RCD behaves quite erratically when all circuits are on, i.e. it sometimes works well on a ramp test and sometimes trips out on half rated. So you'd think that I just change the RCD and everything would be ok. I ordered one of Ebay and fitted it....and got the same problem.
Sorted!
Ok, so I did a ramp test with everything disconnected and it popped out at 25mA then added the circuits one by one and got a leak of only about 3 or 4 mA, that's with all appliances etc connected. Until.... I turned on the final circuit which is an old immersion heater circuit that supplies a lift -then I could barely get the trip to stay on and couldn't get a ramp test reading either. Switched off the isolation switch at the lift end and everything was perfect again.
So I switched everything off and did IR on the lift circuit with the lift isolator switched on.....L/E & N/E were perfect. I then did a ramp test with just the lift on and it tripped at 19mA.
Did the only thing I could do - put the Lift on a separate RCBO and then everything was completely fine!
Thanks for your help people