Rcd As Incomer For Board Isolation

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
May not be advisable for a main CU due to nuisance of everything tripping say when a lamp blows.

But I regularly do this for an economy 7 CU to run a few storage heaters.

 
Well I've had the filament drop down inside a candle lamp and put RCD out.
shouldnt do - the enclosure is all glass, so the only metallic contact with the outside world is the L&N connections. there would need to be some other kind of fault between either L&N to the metallic base, along with an earthed brass holder for an RCD to trip

 
shouldnt do - the enclosure is all glass, so the only metallic contact with the outside world is the L&N connections. there would need to be some other kind of fault between either L&N to the metallic base, along with an earthed brass holder for an RCD to trip
I agree, but it does seem to happen on BC lamps, maybe its cheap lamps or the bottom inside the lamps breaks down tracks to the cap when the lamp blows.

 
can a rcd serve as a main incomer switch on a con unit
If the RCD is a 30mA  one then NOT a good idea as a fault on any circuit could trip everything as the regs highlight. A case of "One out, ALL out!". Not the best idea if a say fault on the immersion heater knocks out the lights too, at night, the customer is elderly etc, etc.

There ARE occasions when you might see a higher rated, say 100mA "time delay" rcd up front as the incomer but it doesn't get away from the fact that circuits may still need 30mA protection elsewhere. Thinking metal cu's on TT earthing system etc.

This, from Hager is a good guide (most makers do a similar guide) also look at the On Site Guide. 

http://download.hager.com/hager.uk/files_download/guides/Consumer%20Unit%20Guide.pdf

If in doubt seek a professional's advice.

 