Hi - hope someone can help.
Installed a new Wylex CCU. Dual RCDs.
When I test the RCDs with the test button - no problem, they both trip.
Testing via my meter at x1In they dont trip.
Testing via my meter at x5In they trip on 0/180 within 18-25ms - so fine.
Insulation resistance tests on circuits >200Mohm except for a couple which are around 6Mohm. (Quite old 20+yrs installation).
r1+r2 all way within tolerances.
CPC continuity all checked out well.
Ze 0.14ohm
Earthing system TNS.
I am using a Dilog 9083P meter which has the plug which can be used for testing RCDs at the nearest convenient socket. But I get the same results if I take cover off CCU and test a circuit directly.
There is a SWA supply down to garden shed with RCD protected sub board - not sure if this is relevant or if discrimination is affecting this in some way.
Both RCDs behave in exactly the same way.
Any advice on what I am missing/or can break this down to diagnose better.
many thanks in advance.
Installed a new Wylex CCU. Dual RCDs.
When I test the RCDs with the test button - no problem, they both trip.
Testing via my meter at x1In they dont trip.
Testing via my meter at x5In they trip on 0/180 within 18-25ms - so fine.
Insulation resistance tests on circuits >200Mohm except for a couple which are around 6Mohm. (Quite old 20+yrs installation).
r1+r2 all way within tolerances.
CPC continuity all checked out well.
Ze 0.14ohm
Earthing system TNS.
I am using a Dilog 9083P meter which has the plug which can be used for testing RCDs at the nearest convenient socket. But I get the same results if I take cover off CCU and test a circuit directly.
There is a SWA supply down to garden shed with RCD protected sub board - not sure if this is relevant or if discrimination is affecting this in some way.
Both RCDs behave in exactly the same way.
Any advice on what I am missing/or can break this down to diagnose better.
many thanks in advance.