In layman's terms please. I'm a retired tree surgeon. Mick
Hi Mick, it was just a load of electrical "electricians" talk. not really related to your problem at all.. It is difficult to explain but i will try..
Basically, in an electrical installation you have to have a means of ADS. That is, "automatic disconnection of supply" which is to take place, [the disconnection that is] within a specified timescale, in the event of an earth fault. This COULD be achieved by means of an OCPD [An overcurrent protection device] like a circuit breaker or fuse.
What we were on about is, say you have a 40A breaker. To get it to operate with the required timescale in the event of an "earth fault" [This is where a phase conductor ["live" if you like, although use of this term in this context is technically incorrect] comes into contact with earth as a result of a fault] [and so, as you can imagine this means that everything else ALSO connected to the earthing system is now ALSO at anything up to full mains voltage] requires a certain amount of current flowing to earth to operate the OCPD in the required time. In the case of the 40A breaker, this would require not be 40A at all, but 200A [or 400A or 800A] depending on the type of breaker you have...
We were on about what would happen if a small generator was the power supply, as your generator cannot possibly put out this sort of current, and so the breaker would not provide ADS, so, therefore, an RCD is fitted to achieve ADS, but in a different way..
What the RCD does is this. It has been established that the MAXIMUM current, [voltage does not matter] that you can have flowing through you, [with a reasonable certainty that it will not kill you] is about 30 milliamps.
Therefore, what an RCD does is this: It compares the amount of current that flows through the one side of the RCD, with that that returns through the other side [thus completing the circuit] In the event that there is a difference of MORE than 30mA it is obvious to the RCD that this current has "escaped" somewhere and so it trips and shuts off the power [hopefully...] I say this because an RCD is a very unreliable device. I believe the failure rate is about 7%.. This is why it is important to test them on a regular basis..
So, as you can see.. The ONLY thing preventing you from being killed by means of electric shock, is the RCD.. Fuses and breakers will not help you at all, [although they MAY prevent overloading and fire] but if you are already dead, this is possibly not much of a consolation!!
Bypassing the RCD would be a BAD idea!!