Because if there is a latent fault elsewhere in the circuit who do you think is going to get the blame when the rcd won't reset?
This has happened to me on more than one occassion where i have protected an entire circuit and had problems elsewhere.Cheers chaps rcd fcu looks the quickest & cheapest option.
Are we not going to be testing our circuit prior to doing the alterations and before re-enrgising.... :C
My BGB has a model MWC form on page 393 with a box headed Part 3 essential tests...
within that box are spaces for insulation test readings between...
Line/Neutral
Line/Earth
amd..
Neutral/Earth
If your Insulation resistance tests are above the minimum permissible...
I fail to see how you are going to get a resistance of somewhere as low as 8000ohms - 7666ohms ish to get a 30ma trip current flowing..???
There are thousands of homes around the country with a single front end 30ma RCD...
a lot installed since the late 70's early 80's.....
and they are not tripping every other week!!!
There really is a paranoia with sparks about RCDs tripping...
If there is a latent defect somewhere in on the circuit, who do you think will get the blame if the homeowner gets a shock from an unprotected part of the circuit??
Oh yeh mr customer will say...
thats the circuit the spark put the new lights onto last month!!
I though he was supposed to of tested it before he added onto the circuit :|
AND..
what do you do when called back in 4 months to stick some wall lights in the bedroom..
oh er!!!
we now need to stick another RCD in..
or undo part of our work we did last time!!!!
ALSO..
leaving an RCD half way down a circuit when it is just as easy to fit it by the CU just makes your insulation tests more of a PITA..
as you got to take it out of circuit... (or not do the full tests!)
Just do a proper job...
test the original circuit..
do the work..
leave a fully protected circuit
:C
just test the dam work properly and stick the RCD near the CU