Can someone tell me when and why would I need to do this test?

Thanks in advance.

 
There is no specific requirement in the regs. But for fault diagnostics, if you think an RCD may be oversensitive, to establish if it trips on too low a fault current would be one instance.

Doc H.

 
A usefull test to have. found on your test meter. (RCD Trip). Mine is a Fluke 1652.

You can just test the circuit (no load), or you can test the circuit with an appliance plugged in and switched on, if you suspect it of having a earth leakage, and this will also show up.

 
A usefull test to have. found on your test meter. (RCD Trip). Mine is a Fluke 1652.You can just test the circuit (no load), or you can test the circuit with an appliance plugged in and switched on, if you suspect it of having a earth leakage, and this will also show up.
what sort of result would you get if you had earth leakage?

 
If you have some "standing" leakage on the circuit, say 10 m Amp and your tester adds leakage gradually (Ramp test) then you will reach the RCDs tripping threshold (normally around 24 m Amps or so) sooner i.e when your meter reads 14 m A.

It is recommended to test with all loads disconnected to get a true reading for the RCD then you could compare it with a loaded reading to see what standing leakage there is.

Or you could use a leakage clamp meter.

 