Hi all I have had a problem reported today about sockets in a property tripping the rcd.
Heres what has happened, the property has had some of the wiring upgraded and a new split rcd fuse board installed. Tests show that the existing wiring was ok to be used and only lighting and a few new power supplies were installed. Tested all of property and all results showing every thing ok so carried on and powered up property and everything ok.
Now after about 2 months a cleaner has been in and their hover is tripping some sockets, so back to see whats going on. Get there and both rcds are down and no power, so power up and ok plug in to sockets and ok:^O, then do in sulation resistance tests and everything clear, power back up and ok so far. Get some more equipment out to see if I can get it to trip and it does only on one circuit controlling 5 sockets through out house ( radial circuit )
split circuit and testing both sides of the radial ok, plug in and trips again. go to first socket in circuit remove the rest of the sockets from radial so only one socket on and ok( but when ever I put the rest of the sockets in to the radial they trip.
so me thinks that fault beyond the first socket in radial but tests are telling me they are ok.
Also on split board when the left hand rcd trips it trips both rcds in the board, but when you manually test the rcds they both trip at once and not seperately what ever one you test.
Thinking this could be a borrowed nuetral but i have checked and i have all the correct neutrals in where they should be.
So haveing a really good day so far and any kind of help from the more experienced would be greatly received. headbang
Heres what has happened, the property has had some of the wiring upgraded and a new split rcd fuse board installed. Tests show that the existing wiring was ok to be used and only lighting and a few new power supplies were installed. Tested all of property and all results showing every thing ok so carried on and powered up property and everything ok.
Now after about 2 months a cleaner has been in and their hover is tripping some sockets, so back to see whats going on. Get there and both rcds are down and no power, so power up and ok plug in to sockets and ok:^O, then do in sulation resistance tests and everything clear, power back up and ok so far. Get some more equipment out to see if I can get it to trip and it does only on one circuit controlling 5 sockets through out house ( radial circuit )
split circuit and testing both sides of the radial ok, plug in and trips again. go to first socket in circuit remove the rest of the sockets from radial so only one socket on and ok( but when ever I put the rest of the sockets in to the radial they trip.
so me thinks that fault beyond the first socket in radial but tests are telling me they are ok.
Also on split board when the left hand rcd trips it trips both rcds in the board, but when you manually test the rcds they both trip at once and not seperately what ever one you test.
Thinking this could be a borrowed nuetral but i have checked and i have all the correct neutrals in where they should be.
So haveing a really good day so far and any kind of help from the more experienced would be greatly received. headbang