Hi people
I carried out a cu change today, on a sunday off all days . It was on a tt system by the way. I upgraded the main earth to 16mm with new stake and upgraded bonding. The ze reading I got was 28.5 ohms. All other test were good, r1+r2, ir tests were fine but im not to sure about the zs readings I got. On the sockets I was getting around 4.5. Not done much testing on tt system so I just wanted to run the zs reading by you guys.
Thanks
I carried out a cu change today, on a sunday off all days . It was on a tt system by the way. I upgraded the main earth to 16mm with new stake and upgraded bonding. The ze reading I got was 28.5 ohms. All other test were good, r1+r2, ir tests were fine but im not to sure about the zs readings I got. On the sockets I was getting around 4.5. Not done much testing on tt system so I just wanted to run the zs reading by you guys.
Thanks