It's on page 26 of the Installation Guide: http://www.rexelrenewableenergy.co.uk/FileDepository/TechDocs/Inverters/SMA%20Sunny%20Boy%20Installation%20Guide%20-%203000TL%203000TL%205000TL.pdfwell, I would doubt the installer has complied with manufacturers instructions,I'd hazard a guess your RCD is 30mA, SMA instructions state a minimum 100mA protection.
I cant remember what page it is, but its there,
"If an external RCD or residual current breaker is strictly required, you must use a switch that triggers
at a failure current of 100 mA or higher."
Yeah I understand that.Yes the RCD will operate as it should thats what the tests would show him, what they dont show is that the RCD split that is supposedly now disconnected is still being fed by the inverter for upto 5 seconds until it shuts down. Understand?
I'll do a bit of reading of the regs posted up by kme so I have the info I need to back up my case.
Can I just clarify....You can't feed the solar pv into a RCBO ....So if I had a full RCBO board I would have to fit a standard MCB for the solar pv connection ?
Cheers.