Hello people
checking a rfc circuit today 2.5/1.5 t&e r1=1.42 rn=1.41 r2=2.33
R1+R2=0.98
my concern is cable length1.42/7.41=191m or am i not calculating it correctly.
Ta
Your calculations appear correct to me...
Assumed lengths of individual conductors from your values of readings should be within a gnats whisker of each other, as they are all in the same cables...
Your total length of individual conductors are:-
r1 = 191.6m
r2 = 192.6m if @ 1.5mm
rn = 190.3m
average length 191.5m
So assuming you got the best part of 200m of cable making up this ring...
What floor area is it covering??
I would guess its a bit bigger than the rule of thumb max 100m2 as per appending 14?
R1+R2 0.98... is that a measured value?
it's not far off the calculated value 1.42+2.33/4 = 0.9375
Whats your Ze? and what type of MCB is on the circuit?
32A B Max Zs is 1.44 @ 80% is 1.15..
1.152 - your 0.98 only leaves 0.172ohms worth of Ze till you are getting high on your Zs.
Well I divide 19.51 by 1000 which gives 0.019 ohms per metre, 19.51 mohm metre
Then R1+R2 / 0.019
19.51 is the miliohms per meter of a single piece of 2.5mm T&E..
if on a ring, 2 x 2.5mm are in parrallel...
so miliohms per meter would be 19.51/2 = 9.755..
so
BES's (0.98 / 9.755)x1000 = 100.46m from CU to furthest point ..
which is in keeping with his 190+m worth of cable used..
My gut feeling this circuit is feeding a bit to large an area.