No parallel paths, conduit, or supplementary bonding. Static caravan, been doing them for years, CPC reading always been 1.67 times reading of line conductors.Are there any parallel paths caused by boilers, water heaters etc...
Is is contained in steel conduit.
Supplentary bonding connected.
Yeah, no spurs.Have you dropped all socket fronts? You may have a spur off to underneath/outside that is bolted to the chassis?
I would go to the mid point and check for a fault or short ,it looks like its half way along your ring , or remove all CPC from the board and test it again, then if you have the same reading test to all other CPC's to see if you have crossed them overi.e. 0.49 of 2.5mm is around 66m
and 0.30 of 1.5 is around 25m
Thanks for the pointers, really appreciated.I would go to the mid point and check for a fault or short ,it looks like its half way along your ring , or remove all CPC from the board and test it again, then if you have the same reading test to all other CPC's to see if you have crossed them over
Any damp in the walls? I chased a similar issue for hours many years ago, to cut a long story short, the new plaster was thick and still damp under the dry skinNo, and don't forget the ring cpc's are disconnected from the met when carrying out an end to end test
Thanks for the pointers, really appreciated.