Are you sure Manator?There is no furthest point on a final ring circuit, as the circuit could be broken at any point to test the R1+R2.
With T&E, R1+R2 must be done from the origin of the supply. The end to end tests and the L & N cross connected tests can be done anywhere on the ring.
Take a sample socket at or near a spur and cross connect at that point. The R1+R2 of the spurred socket would be lower than if cross connected at the origin because the further you go from the Xcon point, the higher the resistance is.
I started last night to put a spreadsheet together to try and test this but it is very confusing with parallel resistances etc. and my limited spreadsheet skills. I might try again when I have time.
Edit; how do you unquote a post? or cancel it? There is a cancel button when editing, but not when posting.