Shared Neutral (not borrowed) 3 phase

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Richard Tawn

Member
Joined
Aug 15, 2017
Messages
5
Reaction score
0
Treading the line, 314.4 of BS7671 states all circuits must be separate,

I look at the following on paper and looks good?

3 pole breaker feeding 3 x single RCD protected (built in) sockets each on a different phase but sharing the neutral (one per machine),

cables are routed via steel conduit,

I am an engineer not a qualifiued electrician ,

I would rather not have to rewire our current setup as cant fit more cable in the steel conduit !

Any takers on the legitamacy of this, as I said it seems to look good on paper as the sockets are connected via steel conduit essentially making them an isolated single 3 phase outlet !

 
Nope, that's not right.

If the 3P+N ran to a sub board first then it would be fine.

If it ran to a machine control cabinet it could be fine (depending on how the machine was wired).

If it is literally just 3 sockets on a wall on the end of effectively a 4 core cable then it isn't actually correct. Electrically it will work, but it is not the correct way of doing it.

 
shared / borrowed are the same thing. the neutral belongs to 1 circuit, the other 2 are borrowing it. its also potentially dangerous if someone isolates 1 circuit and then the neutral is suddenly live one disconnected

 
Do as Lurch said........TPN to sub-board, use rcbos for final circuits & bin the 7288's

 
I would argue it is a single circuit with multiple outlets and therefore I can’t see a problem.


I think the fact it is clearly 3 different single phase BS1363 outlets that is the issue here.

From the one end it is a single circuit because of the TP MCB, but then the socket outlet connected to L1 and N would be on a circuit, which means that L2 & L3 are 2 other circuits.

I wouldn't be surprised if you could actually argue this either way, I'd have to check the book to see what it specifically says.

 
The three pole breaker makes it a single circuit as far as I’m concerned.


The single phase sockets make it 3 circuits for me.

All these years I have been running in 3 neutrals for every 3 radial circuits. You're telling me I should have just been putting them all on a TP MCB and saving myself some cable?

 
Two thoughts:

If anything happened to that shared neutral, (bad connection, etc), any connected loads could be seriously damaged by over-voltage.

If the loads have switching PSUs problems could occur due to third harmonic neutral currents.

 
Anyone else here old enough to remember when it was common for a 3P&N circuit to have a smaller neutral core?

 
Last edited by a moderator:
I know Andy, but final circuits ,  say 3 individual  industrial  sockets   or 3  rows of  lighting  , one on each phase , would need  it's own neutral  .    Thats as I see it anyway , so  although it works , its not technically correct .     Or am I missing something here?

As you say with supply cables ,  we've seen it on a row of houses where the Neutral failed ,  stuff in the houses fried ,  and because snow was on the ground  , you could follow the cable route by the melted snow . 

 
OK lets put this in to another context.

Say I have a 3Ø+N busbar trunking system and I want 3x1Ø+N circuits at various points along its length do I have to install 3 neutral bars?


As I said, I know it makes no odds and it works fine. It's all about what the regs says though.

 
The issue you will have I have brought up before if your memory has not yet failed that badly Tony, is harmonics from the potential loads.

This is why 3.5 core cables have gone away, even on the DNO side.

Harmonics especially triplen harmonics could seriously overload the N, whilst the vector sum of currents may be 0 if the 3 loads are equal, if they are not then the N current will be somewhere other than 0, once you start injecting harmonics then you open a whole new can of worms!

 