headbangheadbangheadbangheadbangDoesn't comply for bathrooms as it does not have an isolating transformer! :_|
headbangheadbangheadbangheadbangDoesn't comply for bathrooms as it does not have an isolating transformer! :_|
Isolating transformer has NO direct path back to earth..I know that, but can you please explain to me how the isolating transformer works? I thought by separating the socket from the mains only a small current could flow protecting the user of said equipment? Have I got this wrong?
the 2.5 would hold up to a dead short. but imagine if the insulation breaks down, and there is 15a flowing through that little cable.... not enough to trip 32A MCB, but enough to trip B6 or blow a 3a fuseYes, that does make some sense. You'd hope a short length of 2.5mm T&E could take the current for the short time to trip the CPD?mmm
how bizarre not one person has sided with you on that decision!I think this has run its course now,outcome is shaver on a ring is fine
fusing it would be better
unless it says in instructions, then we dont know for sure. but either way, they are all better than 32AHow do we know that a B16, B10 or B6 fuse is adequate?
spurring off a socket has fused protection.yeah theres a few reasons, it may ruin decoration, it will add on to the cost + time of the job and I don't need to fuse down for it? Would you call it penny pinching everytime you spured off a socket without fusing?
F'in 5DWI think this has run its course now,outcome is shaver on a ring is fine in the world of 5 day wonders maybe
fusing it would be better
not saying its downright dangerous on a 32A, but it is safer on a 6A (or 3A fuse).If your so eager to prove that a shaver on a 32amp breaker is downright dangerous, prove its safe on a 6 or 10.
so are going to wire this in 6mm then ?Shame on me following regs hey.Steps I don't know who you think your calling a 5 day wonder? I exceed the regs many times day to day, but like you say common sence prevails, and when someone doesn't want decor destroying and there is an easier way round something then it has to be done as long as its to regs.
If you can produce good evidence that a shaver is safe on a B6 breaker please do share, because otherwise we may all be endangering our customers lives by pressuming that one aswell!
Goes back to that reg in the big red book pg 343 'thats how I've always done it, so it must be right'
If your so eager to prove that a shaver on a 32amp breaker is downright dangerous, prove its safe on a 6 or 10.