Hello all
Got my assesment with elecsa next month .changing neighbours consumer unit, shower is rate 7.8kw at 230v = 34a & 8.5kw at 240v =35a 6mm cable from garage to bathroom then buried in wall to shower via isolator. Ok 6mm cable clipped dirct 47a
so 40a mcb but problem is how do i know there is no derating factor i cant see. Put clamp meter on circuit shower up full pulling 34a you would never have on full power as. It would take your skin off so i asked customer what setting they have it and clamped it again 22a max. Question is do i fit 32a mcb to protect cable incase of and derating but then In is not greater or equal to Ib. Would assesor see this as anon compliance or common sense. Customer does no want rewire and cant use other job for assesment.
HELP please
Got my assesment with elecsa next month .changing neighbours consumer unit, shower is rate 7.8kw at 230v = 34a & 8.5kw at 240v =35a 6mm cable from garage to bathroom then buried in wall to shower via isolator. Ok 6mm cable clipped dirct 47a
so 40a mcb but problem is how do i know there is no derating factor i cant see. Put clamp meter on circuit shower up full pulling 34a you would never have on full power as. It would take your skin off so i asked customer what setting they have it and clamped it again 22a max. Question is do i fit 32a mcb to protect cable incase of and derating but then In is not greater or equal to Ib. Would assesor see this as anon compliance or common sense. Customer does no want rewire and cant use other job for assesment.