Hang on here CJS. I don't mean to be rude but your explanation isn't quite clear.No you dont seem to understand there wasn't 238 volts to earth from the SWA there was 238 volts between the SWA and the live line conductors, but the SWA wasn't connected to anything just like a piece of cable lying through the building CJS
I'd be rather wary of doing that, until the source of the 238V is established.Could it be possible, that the cable is acting as a capacitor.Perhpas you could ground the cable ends and the SWA, then test for voltage.
Excellent.I know it's a factory but I'd have a tester across the supply on the cable and flick off each of the circuits on the board individually (where possible) to see if you can isolate where the voltage is coming from.
Not ALL thinking in the wrong direction.........Ok people you all seem to be thinking in the wrong direction. There isn't an induced voltage of 238 volts, if anything it is at 0 volts. The cable is removed from everything so just like a piece of SWA lying through the building and def not touching anything, and the cable is def not damaged in any way.The voltage we are getting is from a live source to the SWA internal conductors, which is NOT connected to anything even the steel wire armouring. So why are we getting the potential difference of 238 volts CJS
:|ARE you saying you put one probe of the volt tester on a live terminal somewhere on the installation and the other probe onto the SWA armour?If yes you would expect the mass of the SWA to act as a crude but poor earth rod and give you the potential difference you describe. No?
of just the general mass of the SWA?Are you saying it is effectively earthing through the air Apache ? I have seen when fault finding panels floating voltages, when circuits are not pulled down to earth.A similiar effect ?
Right... Let me see if I can get me head round what you are saying here.Ok people you all seem to be thinking in the wrong direction. There isn't an induced voltage of 238 volts, if anything it is at 0 volts. The cable is removed from everything so just like a piece of SWA lying through the building and def not touching anything, and the cable is def not damaged in any way.The voltage we are getting is from a live source to the SWA internal conductors, which is NOT connected to anything even the steel wire armouring. So why are we getting the potential difference of 238 volts CJS