I think one of us has missed the point insparkytim's post.
Now I understand his post as a 200A bus bar supply, thus protected by 200A fuses, tapped off without protection to a 63A fuse switch, thus at the load end the tails are limited to 63A (allowing for fuse overload).
Thus the "tails" between the 200A supply and the 63A fuse switch could be sized accordingly to the load limiting of the 63A fuse switch.
You can often fit larger fuses than 63A in a 63A rated fuse switch, so do we allow for this?
I would say NO, we limit the load to 63A, thus we size the "tails" to 63A
I can't quite see the difference here between this and the proposed situation with a 20A & 6A breaker in a CU at the end of the 6/10mm tails?
Thus offering protection limited to 26A (allowing for MCB overload). Yes these 20 & 6A MCB's could be changed for 2 x 63A.
Do we "have" to cater for stupidity every time, remember that we must assess the existing supply for being adequate prior to any changes reg.
This situation is common on bus bar chamber installs, and acceptable. It is also linked to the 3m DNO tails thing. Also there is a reg, but as usual my books are not here, where protection can be provided at the load end.
During a PIR, I have recently seen a 2.5mm sq connected to a 1600A supply no source end protection, protected at the load end of run <1m I can't see how I can fail it.