asked to look at this property / report for a landlord
1: probably under floor next to DB. loose board but lots of boxes i was too lazy to move
2: C3. its a metal board with knockouts and reasonable smooth edges. all cables fixed so movement not really an issue
3: C2. its a 15a carrier into 30a base, but it would be easy to change the carrier to a 30a (the circuit is good for 30a anyway, its the cooker circuit. not the unused shower shower circuit as he thinks it is on SOT)
4: should really be a C2
5: WTGrape
7: er... its TT
9: guidance in an annex, not a regulation so it shouldnt really be noted
12: look on the water pipe?
then there is the schedule of almost no tests
and finally there is a quote to re-wire the place for just under 5K. it only needs a new DB, new feed to kitchen sockets & few other minor issues sorted