i reckon thats at least 6mm armoured
Do an FMEA on it and you'll see why.That's a new one to me as long as one end is earthed it does not matter you are not using the SWA as a cpc
Got one!
if you have a long run that is borderline Zs at the end, then you have a fault, chances are the Zs working back will be too high. not exactly compliant, is it?I understand it is not good practice but to make a statement it is dangerous and not compliant is not true
who cares what you look like with them, as long as your warm. a little too warm at times thoughGot one!
I look like a F fat Jelly Baby...but a warm one!
Not quite the issue.That would have to be a long run to be higher than 1667ohms
SWA often doesnt have RCD protection...That would have to be a long run to be higher than 1667ohms
However this install does :innocentSWA often doesnt have RCD protection...
not much use when it it doesnt work though...However this install does :innocent
Some people just don't see reason and will continue doing things wrong no matter how clearly you explain it to them.and by earthing the swa at the supply end on this tt installation would cause the mcb to trip ? (don't think so)
the swa is only there for mechanical protection and as long as the earth fault loop is not above 1667 ohms then the rcd would trip as I have previously said it is not against the regs and is not dangerous. If it is can someone please tell me the reg as I seem to be missing out on a lot of work as I have come across this loads of times
earth connected at DB................earth connection at banjo fails armour can become live after a faultDo an FMEA on it and you'll see why.
Also look at the physical earth loop paths and include these in your FMEA, then you will understand.
earth connected at DB................earth connection at banjo fails armour can become live after a fault
earth connected at appliance..............earth connection fails armour can become live after a fault
No different unless armour connected at both ends
is this what you mean ? if not let the cat out of the bag and stop with all the cryptic clues and moods.
Do you ONLY do something because the BYB tells you to, or do you sometimes do something because it's good engineering practice?Prodave please im begging you, show me the reg