you could leave as 16A if you wanted
Spur: non-notifiable
yeah i meant dobing in with the circuit thats changed from water spur to skt :xSpur: non-notifiableNew circuit: notifiable
even if your part p reg'd, itll save you notifying!
this job is a wrapGuiness Drinkthanks all. i supose spur in the cu would be better in the 16 amp radial mcb than the ring mcb
wrong terminolgy andy?providing the 50A can protect the cable against fault current, then yes.
no. protect from fault. the shower is a fixed load, it cannot overload. so you dont need any overload protection. you only need to provide fault protection for the cablewrong terminolgy andy?protect the cable from overload better?
Maybe even a 63 amp in ideal conditions.i was thinking the other day, in theory if your ring main was in 6mm u could put it on a 50 amp mcb
you select a cable to take the load.hmm. you select a cable to carry the design current! ?i.e you don't look at the characteristics of the cable to handle xxx current i fault conditions! ?