strange one today..
was called to someones house after stray voltage was measured at the boiler during a service between earth and neutral of 47volts. the engineer believed that this was the fault of why the timer was not working correctly.
At the cu today i took some polarity readings and the results are as follows:
L - N = 230
L - E = 230
E - N = 47v
my Ze was 2.99K ohms and PFC of 1A
previous paperwork records record a Ze of 0.13 ohms and 1.77kA.
when taking the polarity readings the voltage between E & N started to increase when i turned on the boiler and kitchen circuits with all other mcb's off... why would this be????
i have enformed the clients to inform the DNO about the earth readings as it is a TNS installation.
any comments would be useful...