Hi all,
Here is a good one...
I have been installing [over some time] a second DB [fed from a first one, NOT direct from the origin] in a large steel framed shed.
Now, this takes some explaining...
DB one is bolted to the steel work. DB two is on a brick wall [no parallel paths]
Zdb at the first board is .23 ohms
R1 + R2 for the cable BOTH from tables [and also from measurement] is about .266 ohms.
So, you would be looking at a Zs at board two of near enough .5 ohms.
Sure enough, this is what i measured.
SINCE THEN, I HAVE BONDED THE SECOND BOARD TO THE STEELWORK.
A stanchion was 6 inches away, so, i thought i might as well supplementary bond the thing, as if you were leaning on them both and there was an earth fault and the "proper" earth had a high resistance, you would serve quite well as an earth conductor between board and shed.
Anyway, today though, whilst doing something else, i re-measured R1 + R2 This time is it a lot lower, at only 0.9 ohms. Now you would expect that, as now the shed frame forms a "parallel path"
Problem is though, the Zs, at the second board, remains about the same as it was before, WITHOUT the parallel path.
How could this be???
Well and trully confused!!!!!
john....
john....