If you've read my post about the worshop leaky roof then you'll know that I have very tight constraints with turning the power off... basically I can't except for planned work and this is causing me a little bit of difficulty..
Right enough flannel,,,
It's a TNS supply and I'm going to replace the existing sub-main with SWA via a 60A BS1361 metal clad switch fuse... so how do I go about calculationg the Zs?? in my mind I'll have to use the guidance Ze of 0.8ohms..
now this is now causing me a little problem in that the guidance Ze is already above the max Zs of the fuse (which is 0.7ohms), so I guess I'll have to design RCD protection into this sub-main,,
My current thought is that I'll have to put a 80A 100mA 'S' type RCD in the switch fuse instead of the main switch,, what do you recon??