Two jobs back, I fitted a 50mm supp. bond; between a new DB, and the adjacent plumbing services ]
It could technically have been a 25mm; but I didn`t have any around - I did have an offcut of 50mm; so used that.
The only issue that could occur; under exceptional circumstances, would be causation of the PFC to rise above that safely breakable by the OCPDs.
For instance. A 400A(BS88) radial TPN busbar cct; with 36 no. two phase tap-offs installed; each tap-off having a 32A BS88 OCPD.
Each phase of a tap-off feeding a 3-way SP DB (so 72 DBs in total).
These DBs are (mostly) paired up in small enclosures, separating rooms. These enclosures also contain DHW, DCH, flow & return heating, all in copperwork.
4mm supp. bonds were required in all enlosures; running from the MET of each DB, across the 4 pipes, and back onto the other DB in the enclosure.
Now; each individual board used to have a PFC of approx 4.5 - 5.3 KA
but not any more........................
After installing so many bonds; the PFC has risen way above the 6KA rating of some breakers - (separate issue; but some breakers are only 1 or 2 KA anyway {old 3871})
So resolving one issue has caused another - which will have to be picked up on the NEXT inspection..........
(For info - measured Zs at origin = 70KA!!)