Hi again guys :) , question about bonding :) doing a kitchen for a colleague and the only bit I lack knowledge in is bonding requirements. He has a main 10mm2 bond to his water service and one to his gas which is fine, now his cold water feed is going from copper (main pipe) to plastic to supply kitchen items then back to original copper for bathroom, and same idea with his hot water, now my question is will I need to attach supplementary bonding to these pipes or am I just a numpty?

Cheers

Bobby

 
how long is the 'plastic break'?

over 1m then unlikely to be required, contrary to popular belief water is a poor conductor of electricity. Only way to be sure is to do a continuity check between water /gas incoming point and pipework other side of palstic sections, but beware of parallel earth paths - disconnect all other earths at board to ensure a suitable test

 
Last edited by a moderator:
test to see if its extraneous. if yes, bond it, if not, leave it

there can be cases where the entire inside is copper fed from plastic, and you dont need to bond anything

 
No they stop in the bathroom, that's the end of line so to speak, the main line comes in to his kitchen, up the wall a feeds 2 upstair flats as well, and how do I go about testing if it's extraneous?

 
with the increasing use of platic pipe this is an increasingly common problem, but if incomers are bonded most issues are illiminated - do some reading of regs

need a 'wander lead'

 
Last edited by a moderator:
test to see if its extraneous. if yes, bond it, if not, leave it

there can be cases where the entire inside is copper fed from plastic, and you dont need to bond anything
There are plastic sleeved metal gas supply pipes which look like plastic pipes, they are usually straight though. If in doubt...

 
it is sufficient for what you are modifying,(what about lights) but leaves bonding issues as the property will be covered by old and new regs. How old are the electrics?

 
Changing the light switch to a dimmer and new light fittings but the wiring will stay the same, only work im doing is extending the ring circuit to 4 sockets and a 4 grid switch for under counter sockets for washing machine etc.

 
i thought it only needs supplementary if circuits do not have RCD protection,

I would take that as any circuits that might be affected by a potential water leak from the bathroom area (above + below), should have RCD, if not bond it.

Just using a vague memory of the regs and my own opinion.

I then sat back and had to look in the book.  701.415.2.

Sad

 
Last edited by a moderator:
i take reg  to mean if you dont meet the 3 conditions you need you need the bonding.

 
Last edited by a moderator: