If the CU and shed are co-positioned such that a run from the CU to the shed is convenient, then how about this:
Take a spur from a suitable circuit MCB in the CU, down to a high quality (MK perhaps) DPSwFCU. Use this to feed a 2.5 or 4mm (depending on your volt drop calculations) SWA to the shed. At the shed split the incoming supply in a suitable enclosure to feed the sockets directly (overload protection from the FCU in the house) and another SwFCU with a 3A fuse for lights.
You give no indication of the expected loading or the size of the shed, but this will provide plenty enough capacity for most domestic sheds.
# If you take your spur from an existing socket circuit that is already RCD protected, then no need for any more RCDs. If there is a circuit you can use on the non RCD side then add an RCD in an enclosure in the shed just for the sockets.
# in the event of a fault outside, the DPSwFCU can be used to isolate the shed supply from the house untill the fault is fixed.
# the solution is cost effective, no need for mini CUs and MCBs. Keep it simple.
# If you've read up on the ESCs concern regarding overloading of multi gang extensions and have looked at the current / time curve for a 13A 1362, you will know that a 13A 1362 will pass 20A indefinately. So you have effectively provided the client with a 20A supply. Because of this I recommend designing the supply as 20A and using a high quality FCU to be able to cope with this potential overload.
# True, if there is a fault outside it will knock out the house sockets too. But this is a minor inconvenience in the domestic environment and with the DPSwFCU you've taken measures to limit the inconvenience.
# Use the switch on the lights FCU - no extra light switch required (cost effective).
# if this is a "workshop" and there may be rotating machinery, fit HF light fittings.
---------- Post Auto-Merged at 09:54 ---------- Previous post was made at 09:44 ----------
No need to provide the client with a Rolls Royce solution if all he wants or needs is a Mini. You'll just end up pricing yourself out of getting the work.
---------- Post Auto-Merged at 09:56 ---------- Previous post was made at 09:54 ----------
Note that I mentioned using a DPSwFCU - not all FCUs are DP. In fact most (cheaper) are SP. It's a common misunderstanding.