Well first I didn't say you could'nt run a dryer off an fcu ,and why would you be happy with the shed that could possibly pull 20 amps as you say running off a 13 amp yes we no it could but why, just plan it right then it wont have to,O and I'm doing ok thanks on the work front, but in your post you did put well if it takes the power out in the house then it's only a slight inconivence, that's why I like to separate, shed, garage, from main house, end of I'm always up front and tell them the cost, I have happy customers and always straight with them I don't work on cheap an cheerful and if I lose the job then that's the name of the game, move on, my post was not aimed at you or anyone just my opinion on what I would do
Do me a favour - take a breath when you`re posting! I got partway through that, and gave up, due to carp spelling and grammar.
Dunno exactly what you were trying to say, so I`ll just give my thoughts on the OPs question.
I think Batty has alluded to the fact that the customers` intended use has to play a part - your knowledge and experience will tell you what overhead you need to allow in their supply.
If someone had spurred my shed from the ring, I`d be super peeved - I regularly use a chopsaw in the shed, which only uses 2KW - but it is connected to a "combivac", which starts at the same time as the saw, and is rated 1200W.
When I first installed the submain, it was on a B16. Starting the saw drops the breaker one time in three - which is a pain in the rear. Now it has a C20 - which is fine.
I couldn`t have done that from an FCU. But grandad,with his 4` florrie and a DSO for his drill will be fine - I`ve even seen (not fitted) em` as a spur from the ring, with no isolation at the house end.
What we`d have in an ideal world is one thing. What we HAVE to provide is another. The answer is somewhere in between.
Or, if it helps:
1) There is a "Best possible result"
2) There is a "Best result possible"
They can be wildly different; even though they`re the same three words.
KME