Right have been doing an extension which is all done but original house consumer unit is away from meter and fed from 16mm 2 core armoured . This has been moved outside in meter box as it Was in old utility room cupboard and now is playroom. The water has been bonded with 10mm as it is in the old utility room. Any reason armour could not be used as main earth installation is pme. I have used banjo and 16mm to earth block of switch fuse. It was not done originally when switch was inside and would imagine other end is same but as its in a kitchen cupboard cannot get access to reterminate it. I don't like using armour as cpc unless its TT but loop readings are ok although I am going to downgrade fuse to 80 amps as at present its 100amp. Needs doing as 16mm swa won't take 100 amps.