I am looking at the size of swa cable I would need to feed my garage, at sometime in the past someone has used 1.5mm twin and earth hung between the house and garage   

I am looking to feed the garage directly from the cu in the house to a cu in the garage. The garage is about 18 meters away (the garage is only 1.5 meters from the house but the cu is the on the other side of the house), the cable would be run above ground attached to the house wall then, attached to a wall to bridge the gap between the house and garage. In the garage there are 3 double sockets, 3 x 6' tubes, supply to the decking lighting and an outside socket.

Can anyone advise?

James

 
What will the total load be in the garage ?
Mainly power tools drill/ saws 1000w, in winter I might use a 2k fan heater, total lighting will be no more than 250w I do have a spare fridge that might get used, decking lights 3w. Total 3.5k - 4k watts

James

 
OK, some advice,

what is your garage made of?

I'd be looking more at insulation before id be using a 2kW fan heater,

my mate has a well insulated garage, about 25' x 14' and heats it with 2 x 300w tube heaters on stats,

and its never cold in it, ok, so its not warm, but its for working in, not sitting in, he also has a little 1kW oil filled rad for hard winter.

 
Mainly power tools drill/ saws 1000w, in winter I might use a 2k fan heater, total lighting will be no more than 250w I do have a spare fridge that might get used, decking lights 3w. Total 3.5k - 4k watts

James
so you are looking at rough 16A, allowing for a little extra we could call it 20A and run in 4mm. Don't forget RCD protection for sockets, and you need to consider the earthing arrangments.

 
The house is TNCS, I was going to use the earth at consumer unit for the garage.

James
please dont,

its really not that simple,

in fact,

it could be VERY dangerous, lethal even ,

its really not something that should ever be contemplated without a VERY thorough knowledge of the earthing system.

 
Last edited by a moderator:
Looking at it again, I will earth the armour to the consumer unit in the house, leaving the garage consumer unit divorced. Then use a earthing rod to earth the garage. The only external piece of metal is a strip along the top of the asbestos roof which will need earthing, and the is no gas/water pipe. 

James 

 
and does this get Steps approval????? Wouldn't worry about the metal roof strip personally
doing something because you 'think' its what should be done, and not knowing why you are doing it would never get my approval,

the OP appears to be simply doing what he thinks is the consensus with no idea of the implications, or why-fors

 
Looking at it again, I will earth the armour to the consumer unit in the house, leaving the garage consumer unit divorced. Then use a earthing rod to earth the garage. The only external piece of metal is a strip along the top of the asbestos roof which will need earthing, and the is no gas/water pipe. 

James 
Aaaaagh !   He used the A word ............who cares about the earthing ...the roof'll kill ya      ( Apologies:   Butch Cassidy & the Sundance Kid )

 
Last edited by a moderator: