Correct they are from within, so your point is?Neutral currents within the install are not diverted into the install from outside.
You obviously do not understand the terminology I was using, hence my previous posts.
and in a single install proper PME where exactly are the currents diverted from?You think proper pme has no diverted currents?
Well when you loose your neutral because of the pme link, some or all of the current may divert through what ever is connected to your met. If you copper water and gas pipe has a Resistance to earth of 1 ohm and the broken supply is much higher the majority of current diverts. Simpleand in a single install proper PME where exactly are the currents diverted from?
how can you divert your own currents onto your own system?
on my PME my rods are all <3One for you Steptoe, on your pme what resistance to earth do the electrodes along the cne need to be? Thanks
I think you will find that is fault current, NOT diverted current.Well when you loose your neutral because of the pme link, some or all of the current may divert through what ever is connected to your met. If you copper water and gas pipe has a Resistance to earth of 1 ohm and the broken supply is much higher the majority of current diverts. Simple
Hope ive answered your question's. Look forward to your replyHow can a single cable from a Tx to a single consumer be "conventional" "PME"?
So TN-C-S is defined by the number of consumers connected, i dont think so!!
Please explain, in detail.
Whats to explain? What dont you understand?
The Tx electrode is that at the Tx, thus the Star point earth for the Tx.
Not necessarily at the TX, but ill go along with that.
Even IF the DNO drop rods along the SINGLE supply cable from the Tx, this would not make it a PME supply requiring all of the safeguards of "normal" PME as there would be NO possibility of diverted N currents.
Ok, so we have a Dy11from there we have a CNE which is connectred to earth at 2 points or more, if the Pen was to break the current in the consumers install would divide and divert, why do you think we rod the CNE? THE DIVERTED NEUTRAL CURRENT FROM THE INSTALLATION WILL FLOW THROUGH THE INSTALLATIONS MAIN PROTECTIVE BONDING TO EARTH 'T' AND THEN TO THE SOURCE.
1 Tx, 1 Consumer, where can the diverted N currents come from?
From within
Why TT something when you have a perfectly good very low impedance DNO earth?
Im not saying i would, explain your purpose of an additioal electrode and why you feel the Ra is not of to much importance
What are the chances of a broken PEN, risk assessment?
Slim
Also, you need to be careful to understand the subtleties of PME & PME & TN-C-S.
I am aware of them.
Finally for now, got to dash of for a few minutes, it is not definite that the supply is actually TN-C-S, I recently worked on an install "out in the sticks" and I don't do much domestic, that was a pole mount Tx 11kv/400V, which appeared to be TN-C-S, but upon careful checking was actually TN-S, not immediately easy to spot due to the install methods used by the DNO.
Did you ask the design engineer what type of System Earthing was in place?
Ok, which standard are you refering to? So again what requirment is in place with regard to the resistance to earth of the electrodes along the CNE and at which points do the electrodes need to be placed?BTW, it wont go anywhere if you lose the neutral at the head, not unless you have a proper PME , even then, it will depend where your last DNO rod is terminated.
this is why I advocate the use of localised PME where possible.
Thats because andrewedwardjudd, woops i mean chr!s is trolling you & the more you bite ?Chris,
I am far from out of my depth, and once again I find that a poster on the forum ignores my questions and will not answer them, but merely fires questions back at me.
If you took the courtesy to answer the points from previous posts in full then you would get a much kinder response.
Troll LMFAOThats because andrewedwardjudd, woops i mean chr!s is trolling you & the more you bite ?
Well its been a very interesting read I must say, almost action packed :Applaud :ApplaudTroll LMFAO
Well your more than welcome to debate the points raised if you know better, the only contentious issue is that to which sidewinder was angleing too, that of PNB and the Neutral Bond Position which actually presents itself as TN-S, but thats another story.
I will reply in the same manor as other's, if they want to be rude and patronising then so will I!!!
Sidewinder will answer himself when he looks into the purpose of the additional electrode on a PME, why the Ra is important and what current it is that becomes a danger upon a broken PEN, GN5 has a section on it, have a look you may learn something![]()
where is the last point of your PME rodded?Ok, which standard are you refering to? So again what requirment is in place with regard to the resistance to earth of the electrodes along the CNE and at which points do the electrodes need to be placed?
So if the last Point on the CNE had a Electode at 50 ohms and a break occurs upstream, your house has Extraneous conductive Parts with a resistance of 5 ohms, do you really think the current goes nowhere?
Do you need some screen shots of how to use the MultiQuote Button for future reference ?We are now into multiple quoted posts, this always goes wrong for me.
headbangPME is a variant of TNC-S, its how the PEN is Constructed that Makes a TNC-S a TNC-S PME, what is it im confusing,please?
As i have said PME is just a variant of TNC-S