i still think a transformer between 2 lines to give 230v, or the star point as you said, may work
any volunteers to test it?
any volunteers to test it?
To much detail Steps!The way I understand the fluke is it sort of charges a cap to bleed enough current for the Zs test while still keeping the RCD balanced via the N,
So, it NEEDS the N probe on the N to keep the RCD balanced.
I don't think it's possible to test without it.
No star point final load was delta wired.i still think a transformer between 2 lines to give 230v, or the star point as you said, may work
any volunteers to test it?
The RCD is the "main switch" in the board that I can't open.I`m assuming the 4 pole RCD is actually located WITHIN the DB you can`t open?
If its an external RCD & enclosure - then you open it to reveal the Neutral ( if there`s one there!!!!!)
As for the Fluke - it won`t do what you`re asking it to - it has to have a N connection for non-trip mate.
Besides - surely, if the RCD was there, you needed to verify its correct operation, within the required parameters.
The only other option, which might well cook the Fluke, is using another phase conductor for the N - but I`m not convinced that would work, either.
I think you`re stuffed - without 3 biggish, equally sized resistors, to create a star - or another meter![]()
I thought as much,I could not calculate as I could not do an R1+R2!