Thanks for info. Any thoughts on ins res testing on immersion elements?
Thanks.
yep sorry... from your earlier post..
If do insulation resistance on element between live & earth or neutral & earth & reading 0.00M ohms would this mean element breaking down, even if sometimes its not tripping mcb?
First tripping MCB?...
don't get confused between overload & leakage.
e.g.
If an element is breaking down on the neutral side to earth..
there may be no overload thus MCB would not operate..
but there would be leakage & an RCD should trip!
If an element is breaking down on the live side to earth..
most probably a near "live-Earth" short.. and thus overload so MCB will operate!
Second Insulation resistance test to earth should be;
open circuit, OL, or greater than highest value on your meter! e.g. >200Meg etc..
If you are getting a low or 0.00Meg it is a dead-un!
I generally think it is best to disconnect the heater from the circuit..
because there is often a neon back at the switch.. which can sometimes give you a false reading.
Also don't forget about the thermostat switch inside the element this can go open circuit & stop working!
So often best the check each of the three key components:-
1/ Take the heat resistance flex out of the switch / connection box and test across the end of the flex..
sometimes a fault may be in a bit of dodge flex customer has fitted..
non-heat resistant & gone brittle / poor loose connections etc..
had towels & stuff dragged across it and broken down somewhere.
2/ Check continuity across the thermostat..
as you turn the temp adjust bit you can see it go open & closed circuit with your continuity meter.
3/ Check the element. NOTE;
assuming you have proved the continuity of the element approx 20ohm..
with it diss from circuit it is irrelevant which end of the element, (L or N),
you test to earth.. cuz there is only 20ohm between the L & N connection points.