Please could someone explain Touch Voltage to me and do I have to check for it when installing socket outlets and how I go about testing for it
Hi Peetee,
1. Touch voltage is the maximum allowed fault voltage that could appear on exposed metal work if their were a earth fault on that circuit before the protective device operates.
2. Maximum Touch Voltage allowed is now 50volts (used to have 25v on construction sites) as anything above is dangerous to life.
3. The regulations specify the maximum earth fault loop impedance (Ze+R1+R2) allowed for each type of protective to ensure that it disconnects within the given time and to ensure that Touch voltages dont exceed 50volts.
4. If we utilise the formula Volts = currents * resistance and lets give the scenario that we are testing an 30ma RCD on *5 current (150ma then
50volts= 150/1000 * resistance
50volts= 0.150 * resistance
50volts/0.150= resistance
333.33 ohms= resistance
So 333.33 ohms is the maximum Zs (EFLI) that would be possible before a fault voltage of 50v would appear and most modern testers would abort the test so as not to cause a danger to the test operator or anyone else in that building.
Hope this makes sense
Also as high test currents would be needed to check circuit breakers then we dont normally test these, however the manufacturer would do on production.
So what we do is again look in the regs book or onsite guide which will give us the maximum EFLI allowed for a particular circuit breaker or fuse. Then so long as the circuit is installed correctly and EFLI does not exceed the recommended value then we can be sure that the protective device will again disconnect quickly before 50volts is reached on any extraneous/ exposed metal work.