Soul man,
I would have left the cct on the RCD after the changes tbh.
What was the appliance leakage current btw?
I would have left the cct on the RCD after the changes tbh.
What was the appliance leakage current btw?
There's a rule in scientific experimenting. Only change ONE thing at a time.you changed the isolator switch for a completely different one. BUT you never tried it to see if that simple change fixed the fault or not.I dont have a leakage clamp meter, i did IR test the oven and it was clear. I wasn't attempting to mask the problem by putting it over onto the non rcd side, i have been advised to do this, as it was a fixed load and i was surface mounting it. I couldn't see the problem.
Im not saying it is necessary,Steps, zs was within limits so why is rcd protection necessary.
cheers
The cause of the earth leakage should always be investigated firstly, the oven is obviously at fault the leakage could be due to the bad design in installation.Gazza said:Did you try using a time delay RCD? Better than no protection it currently has!