Strange one today.
Lady calls. Triton shower not working. Still in warranty. Triton have just been out, can't fix it, need an electrician.
All that was wrong was neutral incoming connection was loose in terminal and terminal had melted.
Simple fix. New input terminal block. Plenty of slack on incoming neutral to cut back and re terminate on a good bit of cable. Simple 5 minute fix.
Why the heck could the Triton man not have fixed that? He muttered something about "not a standard part". It's their input chock block terminal FFS, surely he has those.
Not complaining, simple fix for an hours money, but if I were the customer I would be very peed off with their service.