Traineeboy
Well-known member
- Joined
- Apr 22, 2020
- Messages
- 201
- Reaction score
- 17
Hi all we were looking at a job today where the customer wants to have a garage consumer unit from sockets and lights. The main house board has a spare way before the RCD with a convenient 32a MCB unused I suggested to chap I was working with to have an SWA from the board at the 32a breaker ( no need for RCD protection there as its mechanically protected) the run 20 meters to the garage where there could be a garage board ( 40 a main switch is a 30ma RCD). Then used earth rod straight from garage CU. I was told that this shouldn't be done and we have to put in a S type RCD at the main house and the RCD at the garage needs to be 100ma. Am I going mad or was not the way I suggested OK ? The earthing arrangement is a PME.
Your thoughts chaps
Your thoughts chaps