Seen at a hot tub install on a tt system. Already installed.
10mm swa straight from c/u off rcbo off a high integrity circuit c/u was a split load wylex jobbie.
Noticed no 100A 100ma s type main switch at front end. Just a 100A double pole switch off TT feed in.
No local rod at tub. So all wired back to c/u but does have local maintenance ip rated isolator adjacent to tub.
Rod sat at an Ra of 38 or is this Ze. Loop at 8.1 from isolator.
So if it's on an rcbo do we now go a max of 1667 ohms or is that only if the front end is protected by 100A 100ma main switch.
Sealed main fuse so just advised 100A.
KA reads 6.9
Not done TT so it's a learning curve here not got a tester for s type rcd.
10mm swa straight from c/u off rcbo off a high integrity circuit c/u was a split load wylex jobbie.
Noticed no 100A 100ma s type main switch at front end. Just a 100A double pole switch off TT feed in.
No local rod at tub. So all wired back to c/u but does have local maintenance ip rated isolator adjacent to tub.
Rod sat at an Ra of 38 or is this Ze. Loop at 8.1 from isolator.
So if it's on an rcbo do we now go a max of 1667 ohms or is that only if the front end is protected by 100A 100ma main switch.
Sealed main fuse so just advised 100A.
KA reads 6.9
Not done TT so it's a learning curve here not got a tester for s type rcd.