However, if an NE fault occurs on a group of circuits that are protected by a double pole RCD and an NE fault occurs it will disconnect the group of circuits, this inconvenience is NOT minimised.
End of.
End of.
a split load board is allowed and minimized.However, if an NE fault occurs on a group of circuits that are protected by a double pole RCD and an NE fault occurs it will disconnect the group of circuits, this inconvenience is NOT minimised.
End of.
You still haven't provided DP disconnection under fault conditions though.a 100ma s type shouldnt trip in a split load board.
the 30ma should trip in 50ms while the 100ma s type shouldnt trip in less than 200ms if i remember right
No, this is very specific to TT,a split load board is allowed and minimized.
under the worst case scenario with two rcd's and an rcbo the rcbo should still have power going to it if the two 30ma rcd's trip.
so your saying practically every domestic install for over 10 years doesnt comply with the regs to minimize inconvenience
a split load board is allowed and minimized.
under the worst case scenario with two rcd's and an rcbo the rcbo should still have power going to it if the two 30ma rcd's trip.
so your saying practically every domestic install for over 10 years doesnt comply with the regs to minimize inconvenience
it was probably allowed because of the cost, rcbo's for say schneider acti9 cost £30 each even for say bg there £18 each compared to £3.50 for an mcbNot really agreed Manator, merely foisted upon us.
Well, not even foisted, just taken as OK without question, whether it was right or wrong.
It was wrong, but no one who had the power, had the guts to question it.
Lord only knows why, because the solution is a total bodge.
The question is: is a dual RCD board compliant, facts are it never has been since its inception! But that's regs for you!
Oh here we go!I think it can be argued that they CAN comply. Not in all situation. The word minimise is relative to the installation.
im just using the acti9 rcbo's as an example i know they have a higher ka rating and comply with 60947, and can have axiliary contacts etc there rated for industrial useAhh, now there is another myth.
Look up the full technical spec on an Acti9 RCBO, some homework for you.
Yes cost is a valid factor, however, not, in all circumstances.
Some requirements are absolute, even though they are not definitively specified in BS7671, this is one of the reasons for the changes in Amd3, these requirements have been in place for over 10 years now, in statute law, but have not been explicit in BS7671 so sparks have ignored them.
Thus something had to be done to force them to comply, because sparks (in general) ignore statute law and only look at compliance with BS7671.
Oh here we go!
the word minimise is not relevant to the installation. Please see the definition http://dictionary.cambridge.org/dictionary/english/minimize#translations
it may be relevant to the number of circuits within an installation.