Hello my name is Andy the NIC EIC help line is closed today so i wondered if anyone could help me please.
I have been working on a barn conversion in South Devon and installed a consumer unit with 30mA RCBO's on every circuit with a 100mA RCD as the main switch and an earth electrode about 4 meters away driven into the ground.
The earth electrode resistance is very high at the moment some 596 ohms!!! the 100mA RCD will not trip out on times 1 but trips out on times 5 at 16ms
When testing one of the three ring circuits the Zs is 64 ohms x1 trips out fine but on x5 the main RCD trips before the RCBO.
Q1 If the earth electrode resistance is reduced will the RCD trip on x1?
Q2 Why is Zs at the sockets so low when RA is so high as main bonding on gas and water pipes are plastic?
Many thanks Andy Johnson.