You'd normaly find the lighting & submains on the 100mA S type & everything else on the 30mA100 mA to protect the Whole Installation and 30 mA to protect individuals
Why would the lighting and submains not be on the 30mA RCD?You'd normaly find the lighting & submains on the 100mA S type & everything else on the 30mA
Under the 16th edition there was no requirement for practically everything to be on the RCD so on a TN-C-S there would be no RCD for lights etc.... The RCD would only be for the sockets usually. On a TT system, as you say you need an RCD to meet disconnection times so a time delayed RCD would have been used in place of the main switch. Still meets the required standard but provides the minimal amount of protection to limit nuisance tripping.Why would the lighting and submains not be on the 30mA RCD?
Sub mains and lighting circuits only require RCD protection if the cables are concealed in walls.Why would the lighting and submains not be on the 30mA RCD?
I wouldn't do it off of the main switch.On a slightly different subject (but still related) - When feeding a consumer unit in, for example, a garage, do the L and N feeding it come from the main switch in the main consumer unit or from an RCD? And would the E come from the MET?
You would wire the supply to the garage CU as a final circuit from the main CU in most cases.On a slightly different subject (but still related) - When feeding a consumer unit in, for example, a garage, do the L and N feeding it come from the main switch in the main consumer unit or from an RCD? And would the E come from the MET?
When you say 'come off a way' do you mean come off a separate MCB?I wouldn't do it off of the main switch.Either come off a way in the CU, using the CU earth terminal, or break into the tails and use the MET.
I've used somebody elses Idea & replied in redWhen you say 'come off a way' do you mean come off a separate MCB?yes, making the submain a circuit of the consumer unit
And what do you mean when you say 'break into the tails'?
Using henley (service connector) blocks you take tails from meter into henley block, then new tails from henley block to house cu & a second set of tails from henley block into switch fuse that in turn runs the submain to garage. Ofcourse the suppliers earth is also connected to as a cpc for the submain but I always TT out buildings
Yes, new MCBWhen you say 'come off a way' do you mean come off a separate MCB?And what do you mean when you say 'break into the tails'?
Depending on the size of the conductors you are using for the garage, you may not be able to fit the conductors in the CU main switch.When you say 'come off a way' do you mean come off a separate MCB?Yes.
And what do you mean when you say 'break into the tails'?
Bit more than a main switch would be required depending on the size of the feed to the garage.I would advise the installation of a main switch at this point so as to be able to isolate both feeds for emergency purposes and compliance with Regulation 537.1.4.
Perhaps the vagueness is confusing.Bit more than a main switch would be required depending on the size of the feed to the garage.I think the vagueness is confusing the issues.
If the supply to the garage is 16mm or smaller then it would fit into most modernish consumer units without too much swearing at it. If for some reason the garage supply can;t be fed from the consumer unit as a final circuit it will often be fed from it's own consumer unit that is connected into the existing tails via a Henley block, which is just basically a large connector block.
You would not just connect the cable to the garage CU straight into the Henley block.
I was on my way back to amend that with some qualifying statements.Your last statement is as bad as Niceguy stating that you can not use an RCD as a main switch. Both sweeping and incorrect.