stemac
New member
Came across a new situation that advice is needed on help appreciated
Added a couple of circuits to a existing installation about 10yrs old on a TT system on a property in the countryside
while doing my live tests at the consumer unitI got a reading of 58v between neutral and earth and 182v between live and earth. This prevented my tester from doing a Ze test (because of the N-e voltage the tester thinks its incorrect)
Went to the meter box pulled the meter tails out of the isolator so no load was present and tested live to neutral 240, L to E 218 and neutral to earth 58volts
the earth was taken directly off the earth rod
the client has experienced no issues of rcds tripping etc
it was suggested by my technical helpline that I call the DNO they arrived and claimed no issues on there side and that it must be a issue with the earth rod as he took a reading of over 200 ohms,
I have experienced the high earth at a rod before but I have not seen the high neutral to earth voltage
when I go back i'm going to use my old tester capable of doing a 2 wire Ze test to get a idea of the earth resistance (using the spike method will be difficult due to paving/tarmac and the fact I don't have the earth probes for the 3 wire method (never had to do that test in 20+ years)
the dno suggested that I bring plenty of earth rods and a breaker and go deep and find a more reputable earth and that will cure the high neutral earth voltage and let me get on,
1 do you think he the dno is right
2 your opinions so that i'm not wasting mine or the clients time in solving the riddle
thanks In advance
Added a couple of circuits to a existing installation about 10yrs old on a TT system on a property in the countryside
while doing my live tests at the consumer unitI got a reading of 58v between neutral and earth and 182v between live and earth. This prevented my tester from doing a Ze test (because of the N-e voltage the tester thinks its incorrect)
Went to the meter box pulled the meter tails out of the isolator so no load was present and tested live to neutral 240, L to E 218 and neutral to earth 58volts
the earth was taken directly off the earth rod
the client has experienced no issues of rcds tripping etc
it was suggested by my technical helpline that I call the DNO they arrived and claimed no issues on there side and that it must be a issue with the earth rod as he took a reading of over 200 ohms,
I have experienced the high earth at a rod before but I have not seen the high neutral to earth voltage
when I go back i'm going to use my old tester capable of doing a 2 wire Ze test to get a idea of the earth resistance (using the spike method will be difficult due to paving/tarmac and the fact I don't have the earth probes for the 3 wire method (never had to do that test in 20+ years)
the dno suggested that I bring plenty of earth rods and a breaker and go deep and find a more reputable earth and that will cure the high neutral earth voltage and let me get on,
1 do you think he the dno is right
2 your opinions so that i'm not wasting mine or the clients time in solving the riddle
thanks In advance